Controller Error Log :
A653 2012-06-19 07:13:55 107 ERROR Critical Error: Fault Type: Page Fault p1: 0x027B647, p2: 0x027A2D6, p3: 0x0278DE8, p4: 0x0000000 CThr: scsi
B853 2012-06-19 07:32:53 107 ERROR Critical Error: Fault Type: Page Fault p1: 0x027B647, p2: 0x027A2D6, p3: 0x0278DE8, p4: 0x0000000 CThr: scsi
page fault ִ ̽ F/W version ϴ ַμ ֽ F/W upgrade ذҼ ֽϴ .
F/W Upgrade Advisory :
ENGINEERING ADVISORY: HP P2000 G3 MSA Controllers on firmware version TS230 might experience a page fault error
Release Date: 2012-02-10
Last Updated: 2012-02-10
Issue Status: Open
DESCRIPTION
In rare conditions an HP P2000 G3 MSA systems running TS230 firmware might experience an unexpected page fault error. To determine if an array has experienced this event, review the array logs and look for the following event.
ERROR Critical Error: Fault Type: Page Fault p1: 0x034BD7E, p2: 0x034BAA2, p3: 0x027E33F, p4: 0x0000000 SCOPE
All HP P2000 G3 MSA array systems are affected by this advisory. RESOLUTION
This issue will be fixed in a future release of TS240 firmware. Workaround
If the above event is found in the logs, disabling the array scrub routine will temporarily resolve this issue until the full fix is available in TS240 firmware. Once the P2000 array is upgraded to TS240, the scrub routine should be re-enabled
|